HVAC system not working

My home unit stopped working yesterday afternoon when it was 114°. Did the usual troubleshooting and cheetah flips but I couldn’t figure it out. Called the Tech and he knew right away where the problem was. Apparently, the condensation drain line was clogged, which tripped the safety circuit, so it wouldn’t flood the system. Flushed out the line and I was up and running again. 🙄
Curious unit is usually completely shutt off if there is an issue like that with drain line, was that the case? Like unit would not run at all, including outdoor one.
 
Some contactors have a cover on them, you have to remove it to be able to push them.

1690067187334.jpg
 
M4AC4030C1000AA, thanks for helping out.
The contactor will be near where the electrical connection is. No high/low pressure cutouts for AC models. If the fan is coming on it’s fine though.

I’m thinking it’s either a compressor problem or low/out of refrigerant. Possibly a TXV problem if you have one…. You’ll have to call someone for those problems.
IMG_8091.jpg
 
@Skippy722 thanks for checking.

How can I validate if compressor is kicking in or no? Because I confirmed all three windings are not shorted and have continuity on them.

Any other thing I can check or troubleshoot before calling da man?
 
@Skippy722 thanks for checking.

How can I validate if compressor is kicking in or no? Because I confirmed all three windings are not shorted and have continuity on them.

Any other thing I can check or troubleshoot before calling da man?
If the fan is kicking on but the compressor isn’t, I think you have a compressor problem. It’s possible a thermal overload switch has failed… I know you said there was continuity but did you check for a short to ground and what was the resistance values?

 
If the fan is kicking on but the compressor isn’t, I think you have a compressor problem. It’s possible a thermal overload switch has failed… I know you said there was continuity but did you check for a short to ground and what was the resistance values?

Did follow the and did not see any short to ground either. Will check actual resistance values too and post here.

Any idea where is thermal switch located?
 
When you turn on the system, you should hear the compressor over the fan. It will be a very obvious 60Hz growl/buzz that gets quieter over the next couple of seconds.
Definitely not hearing it - only fan motor is being kicked on. Thanks
 
Definitely not hearing it - only fan motor is being kicked on. Thanks

You can disconnect the fan wires from the contactor and turn the system for a few seconds if you want to be sure. You'll definitely be able to hear what the compressor sounds like--if it's making any noise at all.
 
You can disconnect the fan wires from the contactor and turn the system for a few seconds if you want to be sure. You'll definitely be able to hear what the compressor sounds like--if it's making any noise at all.
Thanks, can it overheat or kill anything on the compressor ?
 
Thanks, can it overheat or kill anything on the compressor ?

If you ran it long enough without the fan it could overheat the compressor, which would trip the internal thermal switch (which would reset when the compressor cools off) but that would take longer than the few seconds it would take for you to hear if the compressor is doing anything.
 
Okay so tested everything and no issues with compressor.

Changed the capacitor for compressor, initially compressor pipe got cold for a few mins and then nothing(no condensation and not any more cold).

Thermostat is sending voltage and contactor is working well too.
 
Curious unit is usually completely shutt off if there is an issue like that with drain line, was that the case? Like unit would not run at all, including outdoor one.
Yes sir-ree! The entire system did shut down, including the digital thermostat. Like you said, it’s designed to do that to prevent backflow and flooding. I just knew it had to be something simple, but I just didn’t think to look at the drain line. 🤷‍♂️
 
So to follow up on SaberOne's comments about the condensation shut off switch, that is going to be near your airhandler/furnace inside the house, not at the a/c condensing unit outside the house.

Usually a drain pan switch, or a pump cutoff switch, depending on how your condensation drain line is setup.

Since your system started and ran for a few moments, that could either be the switch being tripped, or your system has an issue that is causing the low or high refrigerant pressure switches to trip. Could be a low refrigerant issue.

Honestly, at this point, if you can't locate the condensate drain switch and determine that as your cause, you need to call a professional.
 
So to follow up on SaberOne's comments about the condensation shut off switch, that is going to be near your airhandler/furnace inside the house, not at the a/c condensing unit outside the house.

Usually a drain pan switch, or a pump cutoff switch, depending on how your condensation drain line is setup.

Since your system started and ran for a few moments, that could either be the switch being tripped, or your system has an issue that is causing the low or high refrigerant pressure switches to trip. Could be a low refrigerant issue.

Honestly, at this point, if you can't locate the condensate drain switch and determine that as your cause, you need to call a professional.
I did find the condensate drain switch(rectorseal) outside the coils(furnace area) - cleaned the trap, poured bleach and clean water in it to clear it.

Still suspecting it is something small that is tripping and causing compressor to stop after few seconds.
 
Need a meter with an amp clamp to see if the compressor is pulling amps. The fan itself will pull about an amp.

I dont think you have a contactor issue as the fan wouldn't be running. Also not a drain switch issue either because you have the fan running which means you are getting control power to the outdoor unit.

I'm guessing its low on charge.
 