If the air is moving that fast through the return duct ("sucking it"), then it is too small. With a 15" round duct, you should be moving no more than 1000 CFM on the return side, and that is at 800 feet per minute.
1000 CFM is equal to about a 2-1/2 ton unit, or about a 30,000 btu cooling capacity.
Just for comparasion, both of my home's units are 2-1/2 tons, and I have 24x36 filtered return grilles. The contractor wanted to put in something like 20x20 or the like.
BTW, both of my units are Lennox brand and I wouldn't have anything else. They are quiet and one is going on 10 years and works like new. I have never had any preventative maintenance or other repairs on it. Most people aren't willing to pay the extra $800 for a Lennox, tho.
Make sure you give the "outside unit" (Condensing unit) atleast 42" clear space on all sides, and more than 6' above it.
This will allow almost as much non-restricted air to be pulled through the coils. Ideally, you want 6' of clear space around them.