Staff member
Hello,
As many know, we got a modulating/condensing boiler with indirect water heater. It is all in and working great for the most part. Ive been trying to think through the logic of how best to operate the water heating though since that will be used year-round and so efficiency is important.
The indirect has an aquastat, like any old boiler. You turn the dial to the setpoint, it works a set of contacts to tell the boiler to fire and send water through that zone to heat incoming water.
The boiler logic has a boiler water setpoint of 180F. The water heater is currently set at 125, and has a blending valve ensuring the water stays around 110-115, I believe going to the house.
The water tank temperature is set to prevent bacteria growth. In that it may even be a bit too low. The blending valve setpoint is to prevent scalding, and the boiler water temperature to ensure water heating performance.
My issue is that 180F is getting warm when it comes to operating in high efficiency "condensing" mode. Operating with heater feed water of 130-140F would allow a lot more of a condensing mode operation and still provide some delta T for the water heating operation. I imagine some of this will be just plain trial and error, but what is the smart approach for water heating? 180F factory default? Try to push lower to a more condensing mode of the boiler for efficiency? Is there a water heating (boiler water) temperature that could be too low and help boost the chance for bacteria growth? For example, if the HX surface is a scalding 180F, there will be some localized areas in the domestic water that will be >160F, and therefore the chance of bacteria growth will be much lower?
Maybe Im overthinking this... Our issue is low water pressure and relatively cold water overall with the shower on max temp upstairs. Want to maximize comfort while minimizing gas use and optimizing operations. Any thoughts on this long-winded post?
As many know, we got a modulating/condensing boiler with indirect water heater. It is all in and working great for the most part. Ive been trying to think through the logic of how best to operate the water heating though since that will be used year-round and so efficiency is important.
The indirect has an aquastat, like any old boiler. You turn the dial to the setpoint, it works a set of contacts to tell the boiler to fire and send water through that zone to heat incoming water.
The boiler logic has a boiler water setpoint of 180F. The water heater is currently set at 125, and has a blending valve ensuring the water stays around 110-115, I believe going to the house.
The water tank temperature is set to prevent bacteria growth. In that it may even be a bit too low. The blending valve setpoint is to prevent scalding, and the boiler water temperature to ensure water heating performance.
My issue is that 180F is getting warm when it comes to operating in high efficiency "condensing" mode. Operating with heater feed water of 130-140F would allow a lot more of a condensing mode operation and still provide some delta T for the water heating operation. I imagine some of this will be just plain trial and error, but what is the smart approach for water heating? 180F factory default? Try to push lower to a more condensing mode of the boiler for efficiency? Is there a water heating (boiler water) temperature that could be too low and help boost the chance for bacteria growth? For example, if the HX surface is a scalding 180F, there will be some localized areas in the domestic water that will be >160F, and therefore the chance of bacteria growth will be much lower?
Maybe Im overthinking this... Our issue is low water pressure and relatively cold water overall with the shower on max temp upstairs. Want to maximize comfort while minimizing gas use and optimizing operations. Any thoughts on this long-winded post?