My question really wasn't going to imply that I would be adding'/changing refrigerants, but rather where would the problem lie. While I know that an IR shot on a somewhat corroded pipe won't be precise, it was an approximation with an implied question of what it should be coming out of the unit. Since the totally decomposed rubber insulating sleeve will result in temp loss, is that the whole problem or is the temp at the unit too high at +- 75°, considering ambient outside at the time was 103°?
Plumbers use ID. HVAC guys use OD. Wall thickness is usually 1/8".
A 3/4" plumbing copper is the same size as a 7/8" HVAC pipe.
Reinsulating the line will not help.
75f sounds high.....unless the indoor temperature is high.
In order to tell you what temperature that line should be we would need to know what refrigerant, what type of expansion device, what the indoor temperature is and what the outdoor ambient is.
The refrigerant type will be on the data plate on the unit.
If it is not R22, the answer will be less clear.
Most of the other refrigerant types are charged with subcooling instead of superheat.
The better thing for you to check is the temperature across the evaporator coil.
an 18f-23f drop is in the acceptable range.
You can also check at the return air grille and at the closest supply grille to the unit.
It won't be as exact, but probably close enough.
Let the unit run 5-10 minutes before checking.