I would go 50amp 6 gauge. with a 14-50 then he is ready for his next EV too.@Dadillac OP seems to have gone missing.
My conclusion after you guys did the leg work is his wiring is quite marginal. I would go 30 AMP, 10 G for that one.
Indeed. Notice I wrote THAT ONE.I would go 50amp 6 gauge. with a 14-50 then he is ready for his next EV too.
I believe his current vehicle can charge upto 30amps 240v with the right setup.Indeed. Notice I wrote THAT ONE.![]()
![]()
I didn't see that, maybe it's doing that with in 15 amp set up. Yikes!! Even 10ga would be borderline, true.I believe his current vehicle can charge upto 30amps 240v with the right setup.
so it would be beneficial to his current vehicle too (unless the internets is wrong)
3.7kw is nearly 31A w/ 120V… isn’t this 240v what receptacle did you purchase that’s industrial rated?If I remember correctly the charger in the car is only capable of 3.7kw per hour charging.
Either the clamp or screw connection is fine. Just make sure they're 150% tight ! Since it has the clamp-type connection, it's at least a commercial-grade outlet and those are so much better than residential-grade. I'm not sure what you'll benefit from an "industrial-grade" outlet though.I attached the wire to the outlet with the side plate. Not curled around the screw but placed behind the plate and tightened down
How much did you pay for that one ? I see a $6 one on their website but it only has screw terminals. That's definitely a cheap one and one to avoid and it appears you did.bought a receptacle Leviton 6-20R from Home Depot
Thanks. Someone who gets it. Yeah I always use my #3 phillips on outlets. But I can see how the flat blade would be better. I will definitely do thatI've been an electrician for 36 years and had my electrical license for 20 years. If it isn't a problem with the receptacle or it's connections the problem is in the Volvo supplied cord. Not grounding the box wouldn't cause the issue (although you need to ground the box), and installing a 50 amp circuit with a 15-50R receptacle won't fix it (a 6-20P plug won't fit it). Make sure you use a flat blade screwdriver when making the connections on the receptacle because a phillips screwdriver is worthless for torquing down those combination screws.
https://www.homedepot.com/p/Milwaukee-4-in-2-ECX-Screwdriver-with-Cushion-Grip-MT216/322278393Thanks. Someone who gets it. Yeah I always use my #3 phillips on outlets. But I can see how the flat blade would be better. I will definitely do that
Don
You assume that it is not overheating, when the evidence suggests that it is, in fact, overheating.Okay that is a lot to digest. For the first 4 to 5 months all was well and I never got a stop charge during charging. This is only recently. I am using a 6-20r because that is the plug that is on the cord. If I remember correctly the charger in the car is only capable of 3.7kw per hour charging. So the amperage is pretty low. I am unsure if the fault may or may not be in the charging cable itself. I want to cover my bases before seeing if Volvo will give me a new cable. If memory serves me right I attached the wire to the outlet with the side plate. Not curled around the screw but placed behind the plate and tightened down. I am certain that my run and connections are proper. Was really wondering if not having a ground running from the outlet to the box would possibly cause the heat up. Or if the outlet itself may be the problem. Not sure why y'all are saying I am underwired and such. 6-20R is for 20 amp service. So 12/2 and 20 amp double pole breaker is what is called for and what is installed. If it was drawing more than 20 the breaker will trip. Which it does not. So I assume that the wire is not overheating.
Don
Was really wondering if not having a ground running from the outlet to the box would possibly cause the heat up.
If I remember correctly the charger in the car is only capable of 3.7kw per hour charging. So the amperage is pretty low.