Our house was built in the 1950s, and is mostly 2 prong outlets. A few circuits(garage, kitchen, bathroom) have GFCI installed with "No Equipment Ground" stickers on the plates(as per code, as I understand it). When I've probed those circuits, they do indeed test out as the ground being "dead"(completely open circuit).
Some of the 2 prong outlets are at the end of their useable life(won't retain plugs properly), and I know that often times in older wiring an earth ground is present through the metal fixture box. With those, as I understand, a 3 prong can be installed as long as you properly ground it(either through the outlet screws to the box, or by a short pigtail screwed into the box, or both).
I went investigating in our living room today to see if there's an available earth ground, and what I found I think should have me concerned but I'd appreciate a second look at it, and yes I know that this probably warrants a call to an electrician.
In any case, when I use a multimeter across the two prong, I get 120V as I'd expect
I'd originally checked this with the plate on the outlet by just checking against the plate screw, but the numbers seemed crazy so I pulled the plate and probed a few places around the box on this fixture. What I saw was consistent no matter where I checked.
As I understand it, if the metal receptacle box were grounded, I should measure 0V from the wide plug to the outlet box, and 120V from the narrow one to ground.
This is...not what I get...
Wide to box(or any other metal part of the receptacle, including the plate cover screw) measures ~35V
And narrow to box measures ~95V.
I checked other outlets in the living room(all the same circuit) and they all give this same set of readings. For the others I just checked off center screw.
Obviously I have a problem here that needs to be fixed, but does anyone have any thoughts on what could cause these sort of voltage readings?
Some of the 2 prong outlets are at the end of their useable life(won't retain plugs properly), and I know that often times in older wiring an earth ground is present through the metal fixture box. With those, as I understand, a 3 prong can be installed as long as you properly ground it(either through the outlet screws to the box, or by a short pigtail screwed into the box, or both).
I went investigating in our living room today to see if there's an available earth ground, and what I found I think should have me concerned but I'd appreciate a second look at it, and yes I know that this probably warrants a call to an electrician.
In any case, when I use a multimeter across the two prong, I get 120V as I'd expect
I'd originally checked this with the plate on the outlet by just checking against the plate screw, but the numbers seemed crazy so I pulled the plate and probed a few places around the box on this fixture. What I saw was consistent no matter where I checked.
As I understand it, if the metal receptacle box were grounded, I should measure 0V from the wide plug to the outlet box, and 120V from the narrow one to ground.
This is...not what I get...
Wide to box(or any other metal part of the receptacle, including the plate cover screw) measures ~35V
And narrow to box measures ~95V.
I checked other outlets in the living room(all the same circuit) and they all give this same set of readings. For the others I just checked off center screw.
Obviously I have a problem here that needs to be fixed, but does anyone have any thoughts on what could cause these sort of voltage readings?