Should I tie it to my house ground or a separate ground or just fuhgeddaboutit? Does the job fine without it but..
Need longer than that. 2-3 feet would never pass any inspection. When the soil dries up in the summer, that 2-3 foot rebar is useless.Drive 2 -3 ft of rebar into earth and tie to that using the provided GND lug at noted in the OM.. And no I didn't either, but probably should. My gen is on wheels and get moved around. Now that I think of it my house earth is not too good. I have a drilled well pump and that is plastic pipe so no good to tie to water pipes.
If your transfer panel does not switch neutral, the generator should have its neutral conductor floating, not bonded to the chassis. Having a second bonding point will not prevent the system from working. Your lights will come on, but your safety will be jeopardized. If you are going through the expense and effort to purchase and install a backup power system do it properly.
Take a look at return current flow along the neutral and ground conductors. If you have only three conductors, such as with the neutral bond in the main panel and in the generator (or with just a 3-conductor cord), there will be no separate and independant ground conductor bonding the generator frame back to your house ground. There is a potential of the chassis becoming live as there is current flow along the ground conductor.
Remove the neutral bond and now all return current flowing from the live conductors will flow along the neutral conductor only. It will not flow along the ground conductor. This will ensure the chassis remains at the proper potential.
To meet electrical code requirements for stand alone operation, neutral and ground should be bonded together. This can be accomplished quite simply with a standard 120V 15A plug with ground and neutral jumpered and plugged into an outlet. Picture is here. Many of the Chinese built generators with a built in 120/240V selector do some very odd things with the switch. I do not recommend using the neutral/ground jumper plug with those generators.
My personal opinion (and that of others who I have discussed the issue with) is that floating neutral is safer for stand alone operation. Consider having the generator chassis connected to a suitable ground rod. You are a few feet away, standing in a puddle of water with bare feet. Holding one of the live wires in your hand, there is no return path from the neutral conductor or the other live line through the chassis. With no path for current to flow you will not experience an electric shock. If the output uses a GFCI outlet it will not trip. Let's install the neutral / ground bond again and the return current path exists through your feet to the grounded chassis, through the bond jumper to the neutral conductor. You can be assured of a nasty jolt. If there is a GFCI outlet in place it should open. Which situation is safer? In my opinion floating neutral is better, but the electrical code says it should be bonded. It may seem I'm going against my own advice and I won't tell people to go against code requirements, so follow the rules.
Rewiring will likely void any remaining warranty as well as UL/CSA certification of the generator. In my case warranty is not important, and I feel safety has not been jeopardized in any way. In fact the system is safer now than it was originally.
To determine if your generator uses a floating or bonded neutral perform this simple test. With the engine off, use an ohm meter between the chassis and neutral conductors in the outlet. If it indicates open circuit, the neutral is floating. A short circuit will indicate neutral bonded to ground. I don't recommend doing this to household circuits due to the possibility of exposed AC and damage to the meter.
Don't trust the generator label. I've seen many in which it is incorrect. Confirm for yourself either way.
It is normal for to read very low resistance between the neutral and live terminals on the outlets. You are measuring the DC resistance of the output coils.
Plug in an electrical tester as shown and start the engine. If it indicates open neutral, live/neutral reversed, or live/ground reversed do not use the generator and have someone qualified check the wiring and make the necessary repairs. Use the tester throughout your house to ensure it is wired correctly. This sort of tester is often inaccurate for determining whether the neutral is bonded or not. Even with a floating neutral, the second light will often be on. I suspect this is due to very low leakage currents and a high impedance bulb in the tester.
It's complicated, and depends on how your generator is wired and what type of transfer switch you use. Consult Article 250 of the NEC for detailed info. Also check with your local city or county Building Dept for their interpretation of Article 250.Should I tie it to my house ground or a separate ground or just fuhgeddaboutit? Does the job fine without it but..
One of the most important AND least understood sections of the NEC is the section on Electrical Grounding.
No other section of the National Electrical Code can match Article 250 (Grounding and Bonding) for confusion that leads to misapplication, violation, and misinterpretation. It's generally agreed that the terminology used in Section 250 has been a source for much confusion for industrial, commercial and institutional electricians. Thankfully, this has improved during the last few revisions to Article 250.
Article 250 covers the grounding requirements for providing a path to the earth to reduce overvoltage from lightning, and the bonding requirements for a low-impedance fault current path back to the source of the electrical supply to facilitate the operation of overcurrent devices in the event of a ground fault.
Need longer than that. 2-3 feet would never pass any inspection. When the soil dries up in the summer, that 2-3 foot rebar is useless.
I was under the impression that the GND was for earthing lightning and static discharge. I was citing from the manual for the GP series Generac roll-away portable units.If you're talking about a portable generator, and you're using the 240V, four-prong cord to plug into your house, there is absolutely no need to ground the generator. Your house's electrical system is already grounded (it should already have a ground rod(s) or some other kind of buried grounding electrode). The fourth prong on the generator cord is the ground, which connects to the ground bar in the breaker panel, which is also what your house's grounding electrode connects to. Therefore, the generator is already connected to a grounding electrode. Installing another ground rod for the generator is redundant. What you SHOULD do (and what most people fail to do) is separate the neutral/ground bond on the generator, so you don't have neutral current flowing on the ground wire and conductive surfaces of the generator.
Nice! Just curious how far is your humongous genset to the ufer ? My portable is only ~6kw but my ground array is 40 feet way on the other side of the house. Plus the lugs on the rod are loose from the mower hitting them. I tried to tighten them once but got zapped and the meter started spinning faster. The street xformer is 150 feet down the hill from my panel. I did go around the house looking for mis-wired duplex(s), but didnt find any. I didnt look for GND and N tied in boxes.I have a large 27,000 / 33,000 portable that runs both of my panels. I have a 8awg braded ground from the genset to the house's ufer ground.
Nice! Just curious how far is your humongous genset to the ufer ? My portable is only ~6kw but my ground array is 40 feet way on the other side of the house. Plus the lugs on the rod are loose from the mower hitting them. I tried to tighten them once but got zapped and the meter started spinning faster. The street xformer is 150 feet down the hill from my panel. I did go around the house looking for mis-wired duplex(s), but didnt find any. I didnt look for GND and N tied in boxes.
I was just curious how long the ground strap was. I also never knew that made a portable with wattage rating over 20kw!The genset has a lug that my ground is attached to. The ground wire to ufer has a clip and I just clip it to the ufer. So, I just roll it out and stretch the ground wire and clip it to the ufer. Not sure if thats what you are looking for but that is how I do it.
I have noticed bit of surging when the well pump kicks in.