Quote:
waterpipe ground that goes to a pipe that is not continuous copper through the foundation would NOT check out as a correctly wired outlet via one of those $3 outlet testers, right?
The $3 outlet tester uses a neon bulb. Neon bulbs don't require a very good ground to glow. Certainly, a ground that isn't good enough to trip a 15-amp breaker could make one of those testers light up. And you WANT a ground that can make that breaker trip if a fault occurs.
From the electrical-wiring
http://www.faqs.org/faqs/electrical-wiring/part1/section-31.html FAQ:
One simple way to perform a "real" test is dead short the hot
to ground and see if the fuse or breaker trips. This is,
unfortunately, _extremely_ dangerous. The fuse might explode.
The breaker may malfunction. You may get sprayed with molten
copper. You may start a fire. You may get electrocuted or
blinded. So don't even think of trying this.
One moderately safe approach is to connect a 100W lightbulb
between hot and the ground you wish to test. The lamp should
light fully. If you have a voltmeter, test the voltage between
the ground and the neutral. You should see less than 2 volts.
If the voltage is much higher, or the lamp dims, disconnect it
quickly - the ground may be overheating somewhere. The ground
should be checked for poor connections.