I have a new whole house NG Generac 22kW generator. Although I can change it, the installer left the weekly exercise set to the default 5 minutes. The manual states to leave the mineral break-in oil for 25 hours before switching to full synthetic 5W-20. It's actually unlikely I'll ever need the generator; it's just insurance. 5 minutes seems insufficient to get fully warmed, especially in freezing winter temperatures. I can set the exercise time anywhere between 5 & 20 minutes weekly, bi-weekly or monthly.
If I only ever use it for 5 minutes per week, it will take 5.8 years to hit 25 hours. Obviously, that's not a good idea. The Generac at my previous house had a 10 minute weekly default. Even that would put me at 2.9 years. 15 minute runs times would take 1.9 years. Generac recommends 2-year oil change intervals, but I'll probably go with one-year intervals.
Seems I should switch to 15 minutes weekly, at least until the first oil change, then go with 10 minutes weekly from there. Any recommendations out there? Thanks.
If I only ever use it for 5 minutes per week, it will take 5.8 years to hit 25 hours. Obviously, that's not a good idea. The Generac at my previous house had a 10 minute weekly default. Even that would put me at 2.9 years. 15 minute runs times would take 1.9 years. Generac recommends 2-year oil change intervals, but I'll probably go with one-year intervals.