So my water heater started acting up recently, tripping its 25A breaker. Within a few days it progressed to not only insta-tripping the 25A breaker, but tripping the mains 200A breaker at the same time.
I thought well, its probably a bad element. Its 15 years old, so I figured it was likely due for some. I got two new 4500W elements to match its nameplate rating, and both thermostats along with the internal breaker attached to the upper thermostat.
I had a 30A breaker on hand, and knowing tripping wears out breakers quickly and that it wasnt catching the overload before the 200A breaker could trip, I canned the 25A breaker for the 30A. The wiring is 10 gauge, so this is within spec.
I put all the parts in last weekend and its been running great, until the 30A breaker I put in tripped out last night.
Ive looked at the wiring on the heater 3 times and verified its correct.
From what Ive figured, the upper thermostat controls both elements, as it has a terminal for each. Then both elements connect to the other leg via a terminal on the internal breaker. It looks like when the upper thermostat is 'off' or is satisfied with the temperature, then it supplies power to the lower element all the time, going through the lower thermostat first. If a bunch of hot water is used then it cuts off the lower element to run the upper element.
It would have to switch between them because you couldnt run two 4500W elements on a 30A circuit at the same time...that would be 38A total.
So my best guess is the new upper thermostat is not cutting off the lower element when it runs the upper one. The breaker would probably hold that much of an overload for awhile before finally tripping.
Or nightmare scenario is there is a intermittent fault in the wiring between the heater and panel.
Anything I might be missing?
I thought well, its probably a bad element. Its 15 years old, so I figured it was likely due for some. I got two new 4500W elements to match its nameplate rating, and both thermostats along with the internal breaker attached to the upper thermostat.
I had a 30A breaker on hand, and knowing tripping wears out breakers quickly and that it wasnt catching the overload before the 200A breaker could trip, I canned the 25A breaker for the 30A. The wiring is 10 gauge, so this is within spec.
I put all the parts in last weekend and its been running great, until the 30A breaker I put in tripped out last night.
Ive looked at the wiring on the heater 3 times and verified its correct.
From what Ive figured, the upper thermostat controls both elements, as it has a terminal for each. Then both elements connect to the other leg via a terminal on the internal breaker. It looks like when the upper thermostat is 'off' or is satisfied with the temperature, then it supplies power to the lower element all the time, going through the lower thermostat first. If a bunch of hot water is used then it cuts off the lower element to run the upper element.
It would have to switch between them because you couldnt run two 4500W elements on a 30A circuit at the same time...that would be 38A total.
So my best guess is the new upper thermostat is not cutting off the lower element when it runs the upper one. The breaker would probably hold that much of an overload for awhile before finally tripping.
Or nightmare scenario is there is a intermittent fault in the wiring between the heater and panel.
Anything I might be missing?