Do window/wall AC units have low pressure cutouts?

JHZR2

Staff member
Joined
Dec 14, 2002
Messages
54,966
Location
New Jersey
We don’t run AC a whole lot, really just to cut humidity and heat on the worst days, and sometimes in bedrooms to sleep.

Out home has a wall mounted 24k btu Freidrich AC unit that we run maybe a few times a year. This year we ran it a bit more than usual, and noticed that it started to not be as cool as typical. Filter was cleaned, the unit runs fine, I hear the compressor kick on. But the coil doesn’t get cold.

In other systems, the compressor would not engage if the charge was too low. I don’t know why this unit would have a leak on the sealed system, but it’s something to check. But don’t wall and window units have a similar permissive sensor? Or do they just allow the compressor to run endlessly doing nothing buy burning electricity and itself up?

I do intend to pull the unit and wash the exterior coils. Maybe that’s part of it. But it’s a big annoyance for certain…. Potentially time to install a split in there, though then I’d need to do siding too…
 
I think they typically have the low pres switch.

I use a window AC in my bedroom, despite having a 5T central AC. I like the cold at night but don't want the entire house to be cold in the AM. I seem to go through them every two or three years. Few of them actually work exceptionally well. The latest one, a Midea "U" 12,000 BTU is a standout. Just flat out performs. It requires regular cleaning, more so than others.
 
I wonder why it’s not cooling well then. And unless it’s like boiling a frog slowly, it seems like it was abrupt in terms of changes. I need to put a thermistor on the coil, and a thermometer in the air outlet. Probably need to clean the exterior coil well. Ugh.
 
I wonder why it’s not cooling well then. And unless it’s like boiling a frog slowly, it seems like it was abrupt in terms of changes. I need to put a thermistor on the coil, and a thermometer in the air outlet. Probably need to clean the exterior coil well. Ugh.
It does seem like some real troubleshooting is in order. If you can get a low side gauge on it, that will be informative. But zero cooling suddenly could be a compressor reed valve failure( crack) (if it employs them), expansion valve issue or charge issue
 
It does seem like some real troubleshooting is in order. If you can get a low side gauge on it, that will be informative. But zero cooling suddenly could be a compressor reed valve failure( crack) (if it employs them), expansion valve issue or charge issue
I’m thinking it must be a valve issue.

Here’s the setup:

IMG_6867.webp


When it turns on the compressor runs. And it gets so hot I can’t touch it. But the lines don’t get hot or cold. Only this tiny coiled line gets ice cold.

IMG_6866.webp


The two little ones get ice cold and the big one does nothing.

IMG_6869.webp
 
It appears you are low on refrigerant when you see that.
I think you’re right. Those two small lines are the liquid feed, the big one at the top was the return. The lines had been rubbing and when I messed with it a bit, I started to hear a real leak. I guess it was less than a pinhole, until I touched it.

Going to get the same model to slide in. While I’d like to install a three zone mini split, a 24k+ unit is $$$ and we don’t really run them enough to justify.
 