JHZR2
Staff member
Hi,
I have ran what is likely an undersize extension cord (I believe it is 14G but might be 16), to reach a dehumidifier that Ill be installing a dedicated circuit for... It is in the basement with the breaker box but the opposite side of the basement, so the run is fairly long.
I dont know what the inrush startup current is, but steady state it looks like it pulls about 6A.
My voltage was 117.6 with no load, and once this started, I was at 114.4. This was at the load.
My issue is that the length from my breaker box is about perfect... so there is whatever drop in the wiring. Is that 3.2V drop on a 6A load indicative that the wiring is too small? FYI Im seeing the same 117.6 at other outlets on other circuits, FWIW...
Im tempted to just run 12G and a 20A breaker anyway, just because I have 12G wire...
Thoughts?