@OVERKILL what is the biggest challenge in ramping up gas turbine? is it the thermal mass to be heated before it can reach a temperature to boil the water for the steam turbine? or is it mostly the first cycle direct gas exhaust to turbine boiling? It almost seems like the biggest concern is not addressible by precise control of when to start ramping up (say the grid tell each CCGT to start 5 mins apart) but rather when the sun goes down on each PV and the cloudiness of each site.
Maybe the solution is to have monitoring device on grid connected PV to sent a "brown out soon" signal to the grid and the grid use this to tell which CCGT to start soon?
There are a few different types of combustion turbines available for dispatch.
Aero derivatives like the GE LM series. These are very quick ramping units & can be found in both simple & combined cycle facilities.
HD type units like the GE Frame series can also be found in both simple & combined cycles. These units take longer to start (about 20min) but have much longer service life. Typically they sacrifice a bit of efficiency for greater reliability & extended periods between outages.
Depending on the HRSG, the steam turbine could be fairly quick to come online or take an hour after the CT’s fire. At my last plant it took about 30min to stabilize the boiler feed water circuits & have steam at an acceptable quality to place in service. Could take a bit longer but on a good start about 30min.
As far as dispatching CT’s, the BA employs an EMS computer that takes each generators shift factor, bid spread, ramp rates, etc to calculate the best units to dispatch at every 5min interval(DOT).
Schedule Coordinators & some plant operators will monitor ADS for these dispatch DOT’s with some of these facilities connected directly to the EMS computer through their AGC/regulation system or through other automated systems.
The BA makes minor adjustments throughout the system through AGC/regulation with qualified units. Bid units can have their bids mitigated to help the system as well (dispatch outside of bid spread parameters but within the total mw spread or registered mw limits) when needed.
Generators can curtail min or max production through an OMS card filed with the BA as well. OMS is the outage management system. Certain hydro stations might need a minimum/maximum dispatch for afterbay level control. CT’s might be impacted by gas pressure, air temperature or density, emissions, etc
The PV facilities also submit hourly generation rates based on weather & panel performance. The EMS computer will take the telemetry from the mw meters at every LMP & run calculations from projected to real time & make adjustments to forecasts from there. These are still being updated with syncrophasor technology for much faster response & predictive capabilities on both the BA & TOP sides. This technology is meant to save money to eliminate some of the built in safety bandwidth on the power system. I don’t completely agree with it as I like having a bit of cushion in ratings but that’s where we’re headed. Grid upgrades are expensive & rate payers are already bearing the weight of it. Do to this, decisions were made to come up with a way to push the system to the limits with better predictive analytics. The hope is to be more proactive rather than reactive to system trouble(outages).