GFI protecting outdoor floodlights
You only THINK they are disconnected. There is a wet path to the normally hot conductor somewhere in the line. Some insulation scrape, some lousy splice, something.
Agree. This is a high resistance ground fault. Seems obvious.
100k ohms at 120 v should develop about .0012 amps
Not enough current to trip a GFCI .
I was thinking about that too, but what’s to say that the measurement is accurate? And are gfci just made good enough, or can some be “better”?
So the box under the floodlight is not a single gang box open front and back that is glued to underground conduit. The box continues several inches underground. Maybe a foot or more
I think the box is some kind of outdoor box that you pound into the ground which provides stability for the box and spotlight. Or maybe drop it in a hole and tamp dirt around it. The underground section has openings for UF cable. Probably not conduit.
It's a shame you don't live closer . I think I have a Megger out in the garage somewhere . " Here are the key differences between a megger and a multimeter: "
Is it a rab post mount kit
https://www.amazon.com/RAB-Lighting...hvlocphy=&hvtargid=pla-4584001418532454&psc=1
Piped not so bad pulling new wires if it’s straight uf no bueńo wait till the fall weather
So the way things were installed. The post is in the ground. The wires come up through a opening in the bottom of the post. The post was buried pretty low in the ground and over the years with lawnmowers and weed whackers the covers got beat up. Certainly possible water got into the inside of the post and some could have dropped into the UV cable where the outside sheathing is cut away to expose the wires.
I wonder if that is enough.
Seems odd that both the red and black wire have same resistance to ground. If the UV cable was damaged I might expect one wire to have low resistance to ground but not both red and black.
Here are pictures of the post and wires in the hole. I am thinking water got inside the post, ran down individual wires and into the inside of the UV cable. Maybe it will dry out? Or dig up 5 feet test with megger and splice on a new piece.
So I hired an electrician to replaced the damaged UF cable. I knew I would not get around to digging a trench anytime soon to replace the damaged UF cable.
The electrician said the old Arlington posts were junk and were most likely the cause of water getting into the end of the UF cable.
The new posts are Taymac and the outlet opening is higher and more protected. A lawnmower is unlikely to damage the posts or the outlet cover. And you could order an optional light to replace the sliding cover on the top of the post. Which I did.