Originally Posted By: spasm3
If i back feed my breaker panel through a 220v outlet ( 50amp 6 gauge copper with a neutral ) with my generator , as long as i flip the main breakers off, i should not be sending any power out to the main lines. Am i correct?
Yes, they call those suicide cables! Male on both ends!!!
Here is what you need:
http://www.interlockkit.com/index.htm
From my study, I believe breakers will "throw" in either current direction(it is AC after all) as LONG AS THE BREAKER IS NOT A GFI breaker.
I would run a dedicated double pole breaker for a back feed, and 6 gauge wire it outdoors to a NEMA Generator plug.
Here is a video about the "suicide" cable.
https://www.youtube.com/watch?v=KiByz1E4IBU
I PERSONALLY WOULD NEVER backfeed WITHOUT a interlock kit! Make sure you got all breakers off before you start gennny!!! For example I run 240 from a Honda 3000, 30a NEMA connector, I have to shut off the water heater/outdoor AC compressor, should they come on, it will overload and hopefully trip the double throw backfeed breaker.
----------------
Quote:
If you don't, and have a bad breaker...
I have never encountered a "bad breaker" that will not shut off. They usually get weak and trip all the time, or deteriorate and buzz, never had one that would NOT shut off, about the only way you can make that happen is snapping off the paddle lever!