Originally Posted By: George7941
Inside houses, Romex is fine and no extra protection like flex conduit is needed as long as the wiring is at least 5 feet above the floor. I assume code requirements are the same in a garage, so no flex conduit is needed for an overhead heater.
If you do go with flex conduit, three individual 10ga wires (two insulated and one bare) are preferable to using 10/2 romex inside the flex conduit. 1/2 in flex can easily take 3 10ga wires.
If I go with flex conduit do I need to use solid or stranded wire. While the heater does not really move, I am sure the internal fan will cause it to vibrate ever so slightly.
I bought a 6' whip (to try) that is used for outside A/C but its not really flexible enough for what I need.