Originally Posted by exranger06
Originally Posted by MolaKule
The White wire (Neutral) connects to the internal Ground Bus (Neutral Safety Bus) as does the Safety Ground (bare wire).
This is true only in a "main" breaker panel. If it's a subpanel, the neutral bar/bus is separate from the ground bar/bus. The ground bar is bonded to the panel enclosure, while the neutral bar is to be isolated from the enclosure. Neutral wires for the branch circuits go on the neutral bar, ground wires go on the ground bar. The neutral should be bonded to ground only at ONE point, which is at the first point of disconnect. If you have a disconnect right next to the meter, that's where it should be bonded, and the panel in the house should have separate neutral and ground bars. If there is no disconnect outside and the service goes from the meter straight into the main breaker panel, then the main breaker in the panel is the first point of disconnect and the neutrals and grounds can go on the same bar.
Thanks for the info.
Yes, I was referring to the main breaker box (Main Load Distribution Center) only.
Originally Posted by MolaKule
The White wire (Neutral) connects to the internal Ground Bus (Neutral Safety Bus) as does the Safety Ground (bare wire).
This is true only in a "main" breaker panel. If it's a subpanel, the neutral bar/bus is separate from the ground bar/bus. The ground bar is bonded to the panel enclosure, while the neutral bar is to be isolated from the enclosure. Neutral wires for the branch circuits go on the neutral bar, ground wires go on the ground bar. The neutral should be bonded to ground only at ONE point, which is at the first point of disconnect. If you have a disconnect right next to the meter, that's where it should be bonded, and the panel in the house should have separate neutral and ground bars. If there is no disconnect outside and the service goes from the meter straight into the main breaker panel, then the main breaker in the panel is the first point of disconnect and the neutrals and grounds can go on the same bar.
Thanks for the info.
Yes, I was referring to the main breaker box (Main Load Distribution Center) only.