I'm hoping there's some HVAC guys here that can follow this.
I've got a Lenox condensing unit (LSA090C) that is rated for 7.5 tons and looks to have been installed 1998 - 2004. R22. 3-phase compressor.
Nameplate RLA (Run-load amps?) says 24.7. Not sure if that's all 3 phases added or not. My clamp on meter says each phase is drawing 20 - 25 amps.
Nameplate also says design pressure is 144 / 278 (psi, lo / hi).
I'm measuring about 75 psi on the suction side at the compressor. I haven't measured the high side, I probably don't have a gauge that can do it.
This unit has worked perfectly for the 2 decades that I've owned the premesis, has never had any service (except by me). I seem to have wired-out a high-side cut-off switch, could have been 10 years ago.
Two days ago, something happened. The compressor went into thermal overload. So I cut the power to it. After a few hours I powered it up again, it ran for maybe 15 minutes and cut out again. While it was running, the liquid line between the unit and building was warm, suction line was cold. Ambient temp probably 90. Exhaust air from unit was hot. There was some cooling inside the building, but air didn't seem to be as cold as I remember. Shut the unit down for the rest of the day. Early this morning, ambient was maybe 75, the unit ran for 30 minutes before again thermal overload, shut down.
So Like I said, I measured low-side pressure to be 75. It has a sight glass in the liquid line running beside the unit. Indicator color is green (no legend, I'm assuming green = no water). But I see a fast-moving stream. I guess these are commonly called bubbles? I'm not supposed to see this - right? I'm not supposed to see anything? This would ordinarily mean low charge? But can I have low charge and a correct low-side pressure? Would a low charge cause compressor overload?
Would adding more freon clear up the bubbles, and not raise the low side pressure, and solve the compressor overloading?
Or is the problem in the expansion valve? (it's thermal, with bulb). These are adjustable, is it worth going there?
I've got a Lenox condensing unit (LSA090C) that is rated for 7.5 tons and looks to have been installed 1998 - 2004. R22. 3-phase compressor.
Nameplate RLA (Run-load amps?) says 24.7. Not sure if that's all 3 phases added or not. My clamp on meter says each phase is drawing 20 - 25 amps.
Nameplate also says design pressure is 144 / 278 (psi, lo / hi).
I'm measuring about 75 psi on the suction side at the compressor. I haven't measured the high side, I probably don't have a gauge that can do it.
This unit has worked perfectly for the 2 decades that I've owned the premesis, has never had any service (except by me). I seem to have wired-out a high-side cut-off switch, could have been 10 years ago.
Two days ago, something happened. The compressor went into thermal overload. So I cut the power to it. After a few hours I powered it up again, it ran for maybe 15 minutes and cut out again. While it was running, the liquid line between the unit and building was warm, suction line was cold. Ambient temp probably 90. Exhaust air from unit was hot. There was some cooling inside the building, but air didn't seem to be as cold as I remember. Shut the unit down for the rest of the day. Early this morning, ambient was maybe 75, the unit ran for 30 minutes before again thermal overload, shut down.
So Like I said, I measured low-side pressure to be 75. It has a sight glass in the liquid line running beside the unit. Indicator color is green (no legend, I'm assuming green = no water). But I see a fast-moving stream. I guess these are commonly called bubbles? I'm not supposed to see this - right? I'm not supposed to see anything? This would ordinarily mean low charge? But can I have low charge and a correct low-side pressure? Would a low charge cause compressor overload?
Would adding more freon clear up the bubbles, and not raise the low side pressure, and solve the compressor overloading?
Or is the problem in the expansion valve? (it's thermal, with bulb). These are adjustable, is it worth going there?