I have a Honda EU2000i generator that gets used for power outages, camping, and occasionally construction. I change the oil every 50 hours or 3 months, which ever comes first. It may not need it, but I like to be prepared. I have used Pennzoil Ultra or Pennzoil Platinum 10w-30 since I bought then generator.
I try to exercise my generator once a week or every other week. This allows me to make sure everything is working when I need it and it helps cycle the gas through so it doesn't get stale. I also use Stabil in the gas.
I recently I decided to plug a heater into my generator and load test it. The generator was running fine on my weekly exercise runs, but it had no load on it. When I plugged the heater in the engine rpm's would surge and drop off back and forth. This caused huge fluctuations in the output voltage. I double checked to make sure the heater was not overloading my gen and it was fine.
It ended up being the carburetor was getting gummed up. It was allowing enough fuel through for the weekly test, but when additional fuel was needed to carry the load problems occurred.
The practice of load testing generators is very common in critical power facilities such as hospitals and data centers, but unfortunately most individuals don't do this. I hope this gets every one prepared for hurricane season and approaching winter.
I try to exercise my generator once a week or every other week. This allows me to make sure everything is working when I need it and it helps cycle the gas through so it doesn't get stale. I also use Stabil in the gas.
I recently I decided to plug a heater into my generator and load test it. The generator was running fine on my weekly exercise runs, but it had no load on it. When I plugged the heater in the engine rpm's would surge and drop off back and forth. This caused huge fluctuations in the output voltage. I double checked to make sure the heater was not overloading my gen and it was fine.
It ended up being the carburetor was getting gummed up. It was allowing enough fuel through for the weekly test, but when additional fuel was needed to carry the load problems occurred.
The practice of load testing generators is very common in critical power facilities such as hospitals and data centers, but unfortunately most individuals don't do this. I hope this gets every one prepared for hurricane season and approaching winter.