Originally Posted By: GeneralEclectic
Originally Posted By: JimPghPA
The outside AC unit has the following specks:
Goodman Manufacturing Co.
Well, there's the first part of the problem. Goodman is (I don't mean to be insulting) the bottom of the line. Builder's specials made of generic components. That kind of thing. They're okay as long as they're installed competently, but you can rest assured that they contain the lowest of the low grade components.
Given that, you can probably assume that your compressor does not have a "hard start kit" installed. Because that costs about $100-$200 extra and Goodman would simply never include anything that's not absolutely necessary.
The hard start kit is basically one (or sometimes more) capacitors and a load/speed sensing relay that switches them into a phase-shifting circuit whose purpose is to generate more starting torque while pulling LESS starting current. The idea is that the hard start kit raises the probability of a successful start under marginal -- poor wiring, high source impedance, low line voltage, etc -- conditions. Well, that's basically what you're facing with a generator. The high source impedance part of it.
So, if you're experiencing a heavy load that bogs down the generator, you should probably ring up your HVAC guy and get him to install the kit for your compressor. Assuming that there is one, but there should be.
I can tell you that I have a similar situation. Honda ES6500. Trane 2.5T split high-efficiency heat pump RA ~7A depending. Hard start kit is standard equipment in this. The generator hardly burps when the system switches on.
A second contactor (start relay) for the outside fan with a time delay of a few seconds (probably 4 seconds would be best) would also significantly reduce the total start load. That would give it about 4 seconds for the compressor to start, followed by 4 seconds for the outside fan to start, followed by the existing house air blower motor that already has a delay of 8 seconds after the compressor.