Lawn Mower Keeps Tripping GFCI Receptacle

Joined
May 10, 2005
Messages
3,023
Location
Toronto, Canada
New GFCI receptacle at the front of the house. Lawn Mower trips this one but does not trip the GFCI receptacle at the back of the house.

My question is - would installing a GFCI breaker at the electrical panel help with nuisance tripping?
Leviton GFCI.jpg
 
I would just replace the outlet and see if the new one trips or not.

There are GFCI breakers that are less sensitive, with trip settings of 30 mA, instead of 5 mA. In North America, they're only intended for equipment protection, but in other countries they're often used for personnel protection as well. Using one probably wouldn't be to code, but it should still prevent electrocution at least 99% of the time. Just be sure the trip time isn't over 100 ms.
 
Don't run your lawnmower off a regular circuit sharred with other stuff....especially if it's a 15amp circuit.
Check your breaker box to understand what is what (what else is on the same circuit and the amp rating) if you have not already.
If you don't know or don't have a dedicated 20+ amp circuit....do the below.
Just unplug your fridge and plug into your refrigerator outlet.
You can buy a GFCI adapter that connects to your extension cord also as an easy solution.
You can easily do some damage to your electrical otherwise.
 
I would just replace the outlet and see if the new one trips or not.

There are GFCI breakers that are less sensitive, with trip settings of 30 mA, instead of 5 mA. In North America, they're only intended for equipment protection, but in other countries they're often used for personnel protection as well. Using one probably wouldn't be to code, but it should still prevent electrocution at least 99% of the time. Just be sure the trip time isn't over 100 ms.
If the GFCI receptacle is required by Code ( Outdoors , etc. ) then a 5ma device is required . In the U.S. a 30 ma device is not used for personnel protection and telling people that it's ok to do so is irresponsible .
 
If the GFCI receptacle is required by Code ( Outdoors , etc. ) then a 5ma device is required . In the U.S. a 30 ma device is not used for personnel protection and telling people that it's ok to do so is irresponsible .
I acknowledged that it wouldn't meet US codes, and is less safe than a 5 mA device. I don't see it as irresponsible to suggest a much safer alternative to eliminating the GFCI entirely, which is a common thing to do. Already in this thread we have people who admit to doing this.

30 mA for a short time period is deemed safe enough for European countries, and it's well below the limit where cardiac arrest starts to become possible.

Capture1231.webp
 
I would just replace the outlet and see if the new one trips or not.

There are GFCI breakers that are less sensitive, with trip settings of 30 mA, instead of 5 mA. In North America, they're only intended for equipment protection, but in other countries they're often used for personnel protection as well. Using one probably wouldn't be to code, but it should still prevent electrocution at least 99% of the time. Just be sure the trip time isn't over 100 ms.
For some reason they are more expensive too than the personnel protection gfci
 
A gas lawnmower never trips a GFCI.

Anyplace damp environments are possible, GFCIs are required because at some point, enough people died that it was necessary to protect them from themselves. If swapping the lawnmower and/or the cord do not resolve the issue, call a professional electrician. Don’t become a statistic.
 
We have a fluorescent light that trips the gfci all the time in our basement. I think it’s the second one, I replaced an older one because it did too. Tends to be when they’re on for a long time. Heat related? Arcing? Breakdown? Leakage current?

I get it that the NEC is written in blood. It also doesn’t care how much inconvenience, spoilage, etc. happens.

Some things have exceptions. This one I doubt. So what’s the option? New battery mower? New gas mower? 30mA GFCI?
 
I found a defective wire nutted joint inside the house from where this GFCI receptacle was fed. Cleaned up the wiring and the GFCI does not trip any more.

Don't understand why a bad joint would cause the tripping since any arcing taking place at the joint was not to ground and the line and neutral currents through the GFCI would have been exactly matched. My best guess is that the inductive nature of the lawn mower motor current, along with the arcing causing varying current leads to unbalanced current in the GFCI.
 