Dropped some coin on Inverter Generators, want to break in correctly. Advice?

Joined
Jun 8, 2016
Messages
1,849
Location
Texas, USA
Just bought a Generac 18kw NG/LP generator from Lowes, should be delivered next week. What's the recommended method for breaking one of these in, since it's a constant engine speed? Is varying the load enough? Alternate between powering the house, then powering nothing?
 
Joined
Feb 4, 2020
Messages
315
Location
MI
A neat tip I picked up here on another thread is to use a toaster oven to break in a small inverter generator. The heating element will automatically toggle on and off to vary the load. I thought it was quite clever.
 
Joined
Dec 26, 2005
Messages
18,733
Location
Upper Midwest
Just bought a Generac 18kw NG/LP generator from Lowes, should be delivered next week. What's the recommended method for breaking one of these in, since it's a constant engine speed? Is varying the load enough? Alternate between powering the house, then powering nothing?
Both my Generac automatic standby generator and the portable one had break-in procedures in the owner's manual. Have you looked there? Same question applies to the OP assuming he ever returns to this thread.

For example this is from the standby generator manual:

2.1 BREAK-IN PROCEDURE
Once the unit has been installed and all electrical
checks have been made, it is strongly recommended
that the following "Break-in Procedure" be completed to
ensure correct generator operation in the future.

l . Set the generator's Auto/Off; Manual switch to AUTO.
2. Turn OFF the utility power supply to the transfer
switch using the means provided (such as a utility
main line circuit breaker).
3. The unit will start, and the transfer switch will
transfer to standby.
4. Using the main distribution panel or the emergency
distribution panel (if so equipped), tum on circuits
to load the generator to approximately 25 percent
load and run the unit for one hour.
5. Run the unit for one hour at 50 percent load.
6. Run the unit for one hour at 75 percent load.
7. Run the unit for one hour at 100 percent load.
8. Turn ON the utility power supply to the transfer
switch, which will allow the transfer switch to
transfer back to utility power. The unit will continue
to run for one minute and then shut down.
9. Allow the unit to cool.
10. Drain the oil and remove the oil filter. Replace the
oil filter according to Section 3.4, "Changing the
Oil Filter" (Page 12). Replace the oil with synthetic
oil as recommended in Section 3.3, "Changing
the Engine Oil" (Page 11 ).
11. The generator is now ready for service.
 
Last edited:

4WD

Joined
Sep 21, 2010
Messages
17,961
Location
Texas
None of my Chonda motors … all the way up to 457cc have oil filters … Only my B&S Vanguard has a filter …
Just something to consider in these break-in threads …
 
Joined
Jun 8, 2016
Messages
1,849
Location
Texas, USA
Both my Generac automatic standby generator and the portable one had break-in procedures in the owner's manual. Have you looked there? Same question applies to the OP assuming he ever returns to this thread.

For example this is from the standby generator manual:

2.1 BREAK-IN PROCEDURE
Once the unit has been installed and all electrical
checks have been made, it is strongly recommended
that the following "Break-in Procedure" be completed to
ensure correct generator operation in the future.

l . Set the generator's Auto/Off; Manual switch to AUTO.
2. Turn OFF the utility power supply to the transfer
switch using the means provided (such as a utility
main line circuit breaker).
3. The unit will start, and the transfer switch will
transfer to standby.
4. Using the main distribution panel or the emergency
distribution panel (if so equipped), tum on circuits
to load the generator to approximately 25 percent
load and run the unit for one hour.
5. Run the unit for one hour at 50 percent load.
6. Run the unit for one hour at 75 percent load.
7. Run the unit for one hour at 100 percent load.
8. Turn ON the utility power supply to the transfer
switch, which will allow the transfer switch to
transfer back to utility power. The unit will continue
to run for one minute and then shut down.
9. Allow the unit to cool.
10. Drain the oil and remove the oil filter. Replace the
oil filter according to Section 3.4, "Changing the
Oil Filter" (Page 12). Replace the oil with synthetic
oil as recommended in Section 3.3, "Changing
the Engine Oil" (Page 11 ).
11. The generator is now ready for service.
Thanks for posting that. Mine hasn't arrived yet, but it's good to know that they include a procedure.
Also still trying to decide if I'm going to put it on the east side of the house next to the A/C, which is in very close proximity to the gas line and breaker box, or if I'm going to put it on the patio in the back yard, away from prying eyes. This would require some electrical & gas line running to the back wall of the house.
There's not a crime issue in my area, but I'm horrified at the thought of someone rupturing a pressured gas line to steal the generator.
 
Joined
Dec 26, 2005
Messages
18,733
Location
Upper Midwest
Yeah to reduce the noise exposure to our neighbors the city asked us to put the generator on the opposite side of the house from where the electrical service entrance and the gas line were located. It wasn't that big of a deal in the end, more wire and more pipe of course but nothing major. What cost the most was that the generator required 14" of pressure so the house had to be converted to 2lb pressure with a regulator at each appliance. But even then that whole exercise was only about $800. Perhaps the newer generator sets don't require this any more, I don't know.

The only exposed gas line is the flexible coupling between the house and the generator but if someone did cut that it would certainly leak a lot of gas. But since it is is located on the far side in an alcove of sorts nobody can see we have one.
 
Joined
Dec 28, 2011
Messages
558
Location
key largo,fl
 
Joined
Feb 4, 2020
Messages
315
Location
MI
None of my Chonda motors … all the way up to 457cc have oil filters … Only my B&S Vanguard has a filter …
Just something to consider in these break-in threads …
I agree.
Without an oil filter, the oil needs to be drained to get the glitter out or else it just continues to circulate around inside the engine. That's why so many people recommend short and frequent oil changes during break in.
 
Joined
Jan 4, 2019
Messages
408
Location
Louisiana
Forget the " High octane " gas . Wasting your money . Non ethanol if you wish , and synthetic or synthetic blend oil .
 
Joined
Apr 30, 2014
Messages
788
Location
MN
Fill up the fluids, start the engine, let it warm up for 5 minutes and then hook up a load that'll vary from low load up to around 80%. Let it run for a couple hours then change the oil and put in a good name brand spark plug if it came with the china craptastic sparker. Poor idle quality, surging, poor response to changes in load on the cheaper generators is almost always the junk spark plug they come with from the factory.

Change the oil again after 5-10 hours then follow whatever the manufacturer recommends. I generally use a 5w-40 synthetic HDEO (Rotella T6, Mobil 1, etc...) I've been running a powerhorse 3500w (same as the HF predator 3500) for several years without issue, last weekend I ran it for 4 days straight without shutting down in 90F heat powering my camper with AC maxed out the whole time, load varied between 400 and 2600w.
 

JDebler

Thread starter
Joined
Jul 22, 2021
Messages
2
Ok guys, thanks a ton for the thoughts and opinions. I appreciate it.

The Champion 5500w came with some oil, so I will use that for break in.
The Sportsman 1000w didn't, so I picked up a quart of cheapo Super Tech full synthetic from Walmart. I'll use that up doing break-in changes on both until they drain without sparkles in it.
After that, I will use M1 5W-30 on both, as I have a lot of it on hand for my cars.

I also ordered up some NGK plugs to replace the Torch plugs that came with both.
The Champion is dual fuel, so I will run propane on it as much as possible.

I searched all over and no one seems to make a magnetic dipstick for either one, I am sorry to say. I even ordered some up on Amazon to see if they would fit and I struck out.

The manual for the Champion doesn't have much about break-in:
The first 5 hours of run time are the break-in period for the unit. During the break in period stay at or below 50% of the running watt rating and vary the load occasionally to allow stator windings to heat and cool. Adjusting the load will also cause engine speed to vary slightly and help seat piston rings. After the 5 hour break-in period, change the oil.

The Sportsman manual actually had a bit more info...
You can avoid small engine problems if you follow the break-in procedure below. Because the pistons and rings wear into the engine's walls, small pieces of metal can flake off into the oil. It's important to flush these pieces out of your generator by frequently changing the oil. Maintain at least a 50-75 percent load on your generator for the first 20 hours. (Do not operate the engine at full load during the first 20 hours of operation.) Varying the load will help seat the rings.
1. Allow the engine to run for 5 minutes before adding any load.
2. Change the break-in oil within the first 5 hours of use
3. Do not operate the engine at full load during the first 20 hours of operation.
4. Read and follow the Maintenance/Care section of this Generator manual.

I think I can do a bit better than that, because...why not? Kinda fun, and worth the peace of mind. I think I'll do something like this...
Put oil and gas/hook up to propane.
Run it an hour or so, vary light to medium loads after it is warm.
Change oil after an hour.
Repeat until no glitter in oil.
Pull crappy plug out, put NGK in.
Use it, change the oil at the next 5 hour mark.
Change it again at the manufacturer suggested schedule.
Enjoy powered comfort in a post-apocalyptic world when the time comes.

Thanks again, all.
 
Last edited:
Joined
Feb 4, 2020
Messages
315
Location
MI
Change oil after an hour.
Repeat until no glitter in oil.
I think you'll find that the first 1-hour oil change will have the most glitter, the next 1-hour will have significantly less. After that, I recommend a 5-hour interval and assess the glitter then.

On mine, I did an oil change after the first 10 minutes. Then again at 1, 2, 5, and 10 hours. The 10 hour change looked clean. Every engine is different, so let your eyes be your guide.
 

4WD

Joined
Sep 21, 2010
Messages
17,961
Location
Texas
Ok guys, thanks a ton for the thoughts and opinions. I appreciate it.

The Champion 5500w came with some oil, so I will use that for break in.
The Sportsman 1000w didn't, so I picked up a quart of cheapo Super Tech full synthetic from Walmart. I'll use that up doing break-in changes on both until they drain without sparkles in it.
After that, I will use M1 5W-30 on both, as I have a lot of it on hand for my cars.

I also ordered up some NGK plugs to replace the Torch plugs that came with both.
The Champion is dual fuel, so I will run propane on it as much as possible.

I searched all over and no one seems to make a magnetic dipstick for either one, I am sorry to say. I even ordered some up on Amazon to see if they would fit and I struck out.

The manual for the Champion doesn't have much about break-in:


The Sportsman manual actually had a bit more info...



I think I can do a bit better than that, because...why not? Kinda fun, and worth the peace of mind. I think I'll do something like this...
Put oil and gas/hook up to propane.
Run it an hour or so, vary light to medium loads after it is warm.
Change oil after an hour.
Repeat until no glitter in oil.
Pull crappy plug out, put NGK in.
Use it, change the oil at the next 5 hour mark.
Change it again at the manufacturer suggested schedule.
Enjoy powered comfort in a post-apocalyptic world when the time comes.

Thanks again, all.
I never put gasoline in the tank of my dual fuel … had enough fuel system issues through the years
In fact, have ordered a NG conversion kit to “get off the bottle” 😷
 
Joined
Jan 4, 2019
Messages
408
Location
Louisiana
The manual usually gives you a break in procedure . The ones I've seen say to turn the ECO function off and run it for an hour . Change the oil and you're good to go . No need for a complicated procedure .
 